Any one can help me how much the allowable time required by the standard regarding DGA analysis of transformer oil from sampling to testing.
How much the maximum time frame allowed to make the test valid from sampling to analysis.
On a side note, when filling the syringe, you eject the remaining air bubbles at the end. Over time, a bubble may reappear inside. Don't flush this bubble as it contain gases that were dissolved in the liquid.
IEC 60076-2-2011 Temperature Rise for Oil filled Transformers, It is specified that DGA ( after temperature rise test) shall be done with in 3 days of oil sampling( clause D.4)