ACI318 has rules for conduit placement similar to KootK's list. As for embedded conduits, the electrical engineer is useless, they always tell me size/spacing/layout of conduits is not in their scope, it is the contractor who determines that. So you just go out and after having a small breakdown curled up in the fetal position rocking slowly back and forth when looking at the slab in the area of the electrical room you stand back up and start figuring out how to get it good enough so you can sleep.
We have had success requiring the plumbers and electricians to submit sleeve layout drawings so we can get the bigger opening handled before we get on site, but the conduits are always a problem. They need to be there, so sometimes cleaning them up as in KootK's pic is the best you can do (still a terrible jumbled mess bottom center but better than it started).
I am just barely old enough to get my curmudgeon on, so I still spec slumps but since I am a modern man I will allow deviations at the contractor's request if in my judgement the overall mix still looks good. I see no point in having a stamped mix design or QA program by the supplier.