joengineering
Structural
- Aug 19, 2014
- 59
I have a column that is approximately 40' unbraced but I have wind girts (bent plates) that are attached to the column every 6' on center. I was wondering if these bent plates offer enough strength and stiffness to provide buckling bracing to the column. I have used AISC appendix 6..the Pu on the column is about 300K so it results that I need 1.2K (.004*Pu) of axial compression from the bent plates. These bent plates span 25' and can take the 1.2K in compression no problem. Am I doing this correctly?
JO
JO