ReginaldBoigard
Structural
- Jan 7, 2009
- 5
AISC has limits on slenderness for braces in Specieal Concentrically Braced Frames. Below is section 13.2a.
"Bracing members shall have Kl/r < 4*(E/Fy)^.5
Exception: 4*(E/Fy)^.5 < Kl/r < 200 are permitted in frames in which the available strength of the column is at least equal to the maximum load transferred to the column considering Ry (LRFD) or (1.1.5)Ry (ASD), as appropriate, times the nominal strengthes of the connecting brace elements of the building. Column forces need not exceed those determined by inelastic analysis, nor the maximum load effects that can be developed by the system."
I am looking to use the exception but am having a hard time interpretting the paragraph. I take it that the columns must be designed for the column loads plus some resultant force that would come from the brace failing. The load that would make the brace fail must take into account an overstrength factor and does not use a phi factor. Is this interpretation correct, and if so, would we use the tension or compression brace failure force?
Thanks.
"Bracing members shall have Kl/r < 4*(E/Fy)^.5
Exception: 4*(E/Fy)^.5 < Kl/r < 200 are permitted in frames in which the available strength of the column is at least equal to the maximum load transferred to the column considering Ry (LRFD) or (1.1.5)Ry (ASD), as appropriate, times the nominal strengthes of the connecting brace elements of the building. Column forces need not exceed those determined by inelastic analysis, nor the maximum load effects that can be developed by the system."
I am looking to use the exception but am having a hard time interpretting the paragraph. I take it that the columns must be designed for the column loads plus some resultant force that would come from the brace failing. The load that would make the brace fail must take into account an overstrength factor and does not use a phi factor. Is this interpretation correct, and if so, would we use the tension or compression brace failure force?
Thanks.