Can some of you electrical types help out a civil engineer on airport electrical work?
We are planning on redoing the underground cabling for an airfield and instead of direct bury cable and transformers we are intending to use a ducted system with transformers in pull pits. This has considerable savings for future maintenance especially in the winter.
I'm quoting from the cCanadian Electrical Code which, I am told, is more or less identical to the US code except for metric dimensions.
According to the Canadian Electrical Code Section 74, which considers airfield work unique due to the use of series type circuits, there are some specified dimension for direct bury of the ASLC (airfield series lighting cable) Rule 74-004 gives the minimum bury of 450 mm(18"
. Can this amount be reduced by 150(6"
mm as allowed for by rule 12-012 to 300 (12"
mm if there is mechanical protection? Does PVC type DB-2 satisfy the protection requirements? I note that PE pipe is considered to be mechanical protection.
Rule 74-004 gives the requirement for 75 (3"
mm lateral separation for 6.6 A cables of different series circuits. How does this apply for cables in PVC ducts? Do we need a separate duct for each cable or can we fill a duct to 40% based on cross-sectional area as allowed under 12-1014?
Rule 74-010 (2)(c) appears to allow for groups of cables installed in non-metallic cables. I cannot find any other references to the installation of ALSC in buried ducts.
Can anyone shed some light on the methods and practice for the installation of airfield cables in PVC ducted systems?
Thanks in advance Rick Kitson MBA P.Eng
Construction Project Management
From conception to completion
We are planning on redoing the underground cabling for an airfield and instead of direct bury cable and transformers we are intending to use a ducted system with transformers in pull pits. This has considerable savings for future maintenance especially in the winter.
I'm quoting from the cCanadian Electrical Code which, I am told, is more or less identical to the US code except for metric dimensions.
According to the Canadian Electrical Code Section 74, which considers airfield work unique due to the use of series type circuits, there are some specified dimension for direct bury of the ASLC (airfield series lighting cable) Rule 74-004 gives the minimum bury of 450 mm(18"
Rule 74-004 gives the requirement for 75 (3"
Rule 74-010 (2)(c) appears to allow for groups of cables installed in non-metallic cables. I cannot find any other references to the installation of ALSC in buried ducts.
Can anyone shed some light on the methods and practice for the installation of airfield cables in PVC ducted systems?