Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

air purification unit in OR and AIIR

Status
Not open for further replies.

fatih75

Mechanical
Joined
Mar 31, 2011
Messages
4
Location
BH
hi every body
today my manger bring one company to study of install air purification unit with hepa filter no14 in operating room +AIIR and the salesman tell it is recommended as per CDC ,ISO, and en

is it acceptable to install air purifier in AIIR ,or?
can any body provide me part of this in CDC,ISO,en
what allowable particle per above standard on operating room and AIIR
if tested used laser particles counter
 
How can you tell if an air filter salesman is lying to you?
 
For cleanrooms I design, I typically use ISO class 10,000-100,000; "Grade A-D", with grade A/Class 10,000 being full laminar flow ceiling at 100fpm with low wall returns and 100+ ACH. Find out the classification for your room, then see if the HEPA will obtain that cleanliness level. I prefer Flanders and Camfil Farr. Don't trust the salesman whatever you do. This is an area where you really need an engineer who designs cleanrooms. You do not sound like you know much about HEPA filtration. Be cautious.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top