Many pressure sewer pipe and fitting products will state that they are only designed for liquids. Most installation procedures call for all air to be evacuated from a pipeline prior to acceptance pressure testing. To do this, the pipeline must be filled slowly (1 to 2 ft/s fluid velocity), and air release valves must permit the air to escape from the line during filling. Beware that small air pockets may remain at high points throughout the pipeline. These air pockets may have to be coaxed to the valve location using the fluid flow. Failing to remove air from the pressure sewer line is dangerous. Since air is compressible, a large amount of stored energy is present when the line is under pressure. As well, transient surges may be greatly amplified by the presence of air pockets within the pipeline. (The air pocket reduces the cross sectional area available for fluid flow, which in turn increases the fluid velocity.)