air flow calculations 2
mpullin
I am trying to figure out how much air flow is going through a square duct. I have airfoils in line and measuring differential pressure across them. I have the range of the transmitter but don't know how many inches of differential is equivilant to lbs/hr. I have tried to find venturi calculations but have only come up with calculations using pipe diameter. I do have the dimensions of the duct. But other than the specified information, I don't have a whole lot. I would appreciate if anybody could point me in the right direction.
Check out the thread and posting in HVACR engineering Thread403-157067 It has a link to Dwyer Instruments and some helpful formulas.
I'm not a real engineer, but I play one on T.V.
A.J. Gest, York Int.
Let me know if that helps the thread runs a little long but the Dwyer site has good data
mpullin,
Your description is a bit sketchy. Differential pressure across some airfoils is not enough to calculate flowrate. If you have a venturi tube, then it's easy and accurate and I can point you to the formulas.
If not, there are a lot of ways to measure airflow. The Dwyer site is a good start. The best method depends on the accuracy you need and the velocity range you expect.
ko (
Thanks for the replies. They were a big help. I have found calculations for the velocity and have figured that out. I am working on a mass flow calculation now and the number I am coming up with is a little to high in my opinion. I am still working on it and will eventually get it. But I would appreciate if any direction could be given.
Are you using a pitot tube? Just be aware they are very inaccurate below 600 ft/min or so. Otherwise, finding massflow is easy:
1. Get average velocity by profiling at regular points over a cross-section of your tube (Dwyer and others have guidelines)
2. Volume flow = average velocity x section area (example: ft3/min = ft/min x ft2)
3. Mass flow = volume flow x air density (example: lb/min = ft3/min x lb/ft3).
You can use this tool to find density:
ko (
Thanks for all the help that I have recieved. With the help of your post I have calculated all my measurements. Now I have to incorporate my calculations.
Thanks again.
When you average air velocity thru ducting be sure measurements are in a uniform air flow and be aware that the velocity distribution may be parabolic. Read the instructions supplied by the manufacturer of the pitot tube to calculate average velocity.