Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Air conditioner electrical protection

Status
Not open for further replies.

jose luis

Electrical
Nov 11, 2016
1
Hi, in my country most of the air conditioner installers are using 2 one phase breakers (110v) to protect the 220 v air conditioners, instead of use a two phase breaker in 220 v, is this practical correct, which are the risks of this action?, Thanks
 
Replies continue below

Recommended for you

We used to use two breakers with a handle tie.
The reason for a two pole breaker is mostly but not all a matter of safety.
With two single pole breakers an overload or fault may leave one breaker still energized.
This may pose a hazard to a repairman who doesn't realise that one line to the inoperative A/C is still hot.
There may be a rare instance where a winding goes to ground internally and initially trips only one breaker leaving the motor energized by the other line with the return path through the ground fault. This will in most instances sooner or later trip the second breaker.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor