AFT Fathom Question

Status
Not open for further replies.

Josh2008

Mechanical
Joined
Sep 25, 2008
Messages
42
Location
CA
Good Afternoon,

I was wondering if anyone would be able to explain how I would model a simple circuit (attached picture) to calculate split flow in AFT. I don't know which icon is used to drain water to atmosphere. Can I simplify this in AFT or do I have to include a pump and reservoir, etc?

Thanks,
Josh
 
Out of my "LEAGUE"
I use Stoner PLS.

17-1058074210T.gif
 
Josh,

The outlet of your pipes could be a pressure node with outlet pressure set at atmospheric pressure. Alternatively you could add a valve node and designate it as an "exit" valve or use the spray discharge.

 