I forgot to mention that this delta-wye bank that Ohio Power has with 1 transformer larger than the other 2 feeds a large restaurant in Canton, Ohio. This transformer bank has withstood 2 instances or the supply substation losing a phase on the 138,000 volt side of the substation.
Both Duquesne Light Company and Ohio Edison have 2,400Y4,160 volt distribution systems and 3-wire wye primary 3 or 4-wire delta distribution transformer banks work fine on these systems.
You third world utility has more problems than that there are delta-wye distribution transformers. The things were probably hooked up wrong in the first place.
Interestingly, a 4-wire wye primary 3-wire delta secondary is sometimes used as a grounding autotransformer to refit say a 13,200 volt delta secondary substation winding so that it will act as a 7,620Y13,200 volt source. Ohio Power sometimes will do this with a 138,000Y79,674 primary 69,000Y39,837 secondary 13,279 delta tertiary transmission transformer. A 7,620Y13,200 volt 4-wire wye primary delta secondary transformer is connected to the delta tertiary to obtain a neutral for 7,620Y13,200 volt distribution. In some instances a small 7,620Y13,200 volt floating neutral wye primary 4-wire delta transformer is the only load on the 13,200 volt delta tertiary and the small transformer supplies internal power for the station relays and operating controls.
Also, when a 3-transformer bank is operating 3-wire wye primary 3-wire delta secondary a single phase secondary load divides 2/3 into the transformer that directly connects to the single phase load and the other 1/3 of the current through the other 2. There is a similar relationship for 120 volt loads on a 120/240 volt 4-wire delta secondary.
Wye-delta transformer banks DO NOT present problems if you are using proper design, installation, and repair procedures such as cutting the other 2 phases and grounding all 3 before repairing a downed wire.
Sounds a lot to me that when this third world customer upgraded a wye-delta bank from 2 transformers to 3 they forgot to isolate and insulate the neutral point of the primary neutral.
Cleveland Public Power also uses the wye-delta configuration on their 7,970Y13,800 volt distribution and they use both 2 transformer and 3 transformer banks. They do not have any problems with these.
Oh, First Energy, Ohio Power, and Duquesne Light Company have considerable amounts of rural distribution and do not have these kinds of problems.