Advanced Meter Installation

Status
Not open for further replies.

GMIEE

Electrical
Mar 10, 2008
14
When choosing a type of advanced meter to install, would you recommend socket mount meters either directly on or near the transformer feeding a building or would you go for installing a panel mount meter in the existing main distribution panel?

I am wondering about the pro/cons of each setup.
 
Replies continue below

Recommended for you

On the transformer makes transformer replacement more difficult.
 
Revenue meter location will be dictated by the utility. The main service panel or main distribution board is a good location for owner meters. You will have a larger selection with panel mount meters. Many of the larger breakers have metering built in or available as an option. You can scroll through a wide range of parameters. Check your breaker catalogs for the options available.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 