On a current project, I specified Simpson AT-XP acrylic adhesive be used to anchor large silos to the concrete foundation. This product is approved for installation down to 14 degrees Fahrenheit. However, where we are, temperatures are already below this for extended periods so the contractor has requested to use Simpson AT acrylic which is approved down to 0 degrees Fahrenheit. This is where my question arises.
The AT-XP (originally specified) meets strength design provisions of ACI318 Appendix D. However, the AT (requested substitute) does not as it is only has ASD design methods listed. If the AT adhesive has sufficient capacity to anchor the silos to the base under service loading, would it be an approved substitute? Or should it automatically be rejected due to it not meeting strength design provisions?
The AT-XP (originally specified) meets strength design provisions of ACI318 Appendix D. However, the AT (requested substitute) does not as it is only has ASD design methods listed. If the AT adhesive has sufficient capacity to anchor the silos to the base under service loading, would it be an approved substitute? Or should it automatically be rejected due to it not meeting strength design provisions?