Electrical
- Jan 22, 2012
- 11
We have a Captive Power plant of 18 MW Capacity.The generation is at 11KV and after catering to our plant requirements the excess power is being sent to the 66 KV grid through a YNd1 66KV/11KV,20 MVA transformer bank.When the CPP is under maintenance or not operational the grid power,stepped down through the same transformer is being used to supply our plant load.
Now we intend to install a second CPP of 8 MW Capacity and a seperate transformer of YNd1 66KV/11KV,10 MVA Transformer.The two transformers will be connected to the 66 KV grid through a common bus but at 11 KV side they will not be connected.Both the Captive power plants will be sepperately connected to the grid through their respective transformers so in fact the transformers will never be operated in parallel though both are connected to a common bus at the HV Side.My question is:
1) Will there be any circulating currents between the transformers at the 66 KV Side.The neutral is solidly grounded and the percentage impedence of the transformers are exactly equal.
2)The generators and transformers are not paralled at 11KV.So the possibility of circulating current between the generators(star connected with low resistance NGR) can be ruled out?
3)We intend to run the generators in parallel only when the 10 MVA Transformer is not in line ie.So in this case the generators are operating in parallel and synchronised with the grid through a single transformer only ie..20MVA.In this case please let me know if we need to isolate the neutral of one generator.Both the generators are star connected with low resistance neutral grounding resistor along with motorised isolator.Both the generators are 2/3 rd .pole pitched .
Now we intend to install a second CPP of 8 MW Capacity and a seperate transformer of YNd1 66KV/11KV,10 MVA Transformer.The two transformers will be connected to the 66 KV grid through a common bus but at 11 KV side they will not be connected.Both the Captive power plants will be sepperately connected to the grid through their respective transformers so in fact the transformers will never be operated in parallel though both are connected to a common bus at the HV Side.My question is:
1) Will there be any circulating currents between the transformers at the 66 KV Side.The neutral is solidly grounded and the percentage impedence of the transformers are exactly equal.
2)The generators and transformers are not paralled at 11KV.So the possibility of circulating current between the generators(star connected with low resistance NGR) can be ruled out?
3)We intend to run the generators in parallel only when the 10 MVA Transformer is not in line ie.So in this case the generators are operating in parallel and synchronised with the grid through a single transformer only ie..20MVA.In this case please let me know if we need to isolate the neutral of one generator.Both the generators are star connected with low resistance neutral grounding resistor along with motorised isolator.Both the generators are 2/3 rd .pole pitched .