pmour
Civil/Environmental
- Jul 1, 2005
- 10
Link
All references are to ACI 318-05.
It the above link it is clarified that the minimum flexural reinforcement is not controlled by the provisions of ACI 10.5.1 and 10.5.2 as they do not apply to structural slabs and footings of uniform thickness, rather the minimum flexural reinforcement is determined by 10.5.4 as 0.0018bh. For a structural slab having top and bottom reinforcement both of which exihibit flexural tension, this minimum flexural reinforcement of 0.0018bh for each layer would control over the temperature and strinkage reinforcement of 0.0009bh for each layer (0.0018bh/2).
My question: Is the provision of 10.5.3 applicable also?
If not, As minimum would always be 0.0018bh for each layer.
If so, and in the situation where the required As is small enough, the minimum flexural reinforcement determined by 10.5.3 as 4/3 * As,reg could be less than that determined by 7.12 as 0.0009bh for each layer, thus As minimum being 0.0009bh for each layer.
Another way to write it (applies to slabs and footings having top and bottom steel):
If As > 0.0018bh, use As
If As < 0.0018bh < 4/3As, use 0.0018bh
If 0.0009bh < 4/3As < 0.0018bh, use 4/3As
If 4/3As < 0.0009bh, use 0.0009bh
All references are to ACI 318-05.
It the above link it is clarified that the minimum flexural reinforcement is not controlled by the provisions of ACI 10.5.1 and 10.5.2 as they do not apply to structural slabs and footings of uniform thickness, rather the minimum flexural reinforcement is determined by 10.5.4 as 0.0018bh. For a structural slab having top and bottom reinforcement both of which exihibit flexural tension, this minimum flexural reinforcement of 0.0018bh for each layer would control over the temperature and strinkage reinforcement of 0.0009bh for each layer (0.0018bh/2).
My question: Is the provision of 10.5.3 applicable also?
If not, As minimum would always be 0.0018bh for each layer.
If so, and in the situation where the required As is small enough, the minimum flexural reinforcement determined by 10.5.3 as 4/3 * As,reg could be less than that determined by 7.12 as 0.0009bh for each layer, thus As minimum being 0.0009bh for each layer.
Another way to write it (applies to slabs and footings having top and bottom steel):
If As > 0.0018bh, use As
If As < 0.0018bh < 4/3As, use 0.0018bh
If 0.0009bh < 4/3As < 0.0018bh, use 4/3As
If 4/3As < 0.0009bh, use 0.0009bh