JAE
Structural
- Jun 27, 2000
- 15,590
In ACI 350-06, I have to calculate an Sd factor from section 9.2.6 (equation 9-8) which lists:
Sd = [φ]fy / [γ]fs
Where
[φ] = 0.9 for flexure
fy = 60 ksi for rebar
[γ] = 1.4 (for my fluid load combination 1.4(D+F))
fs = service level stress in the rebar
The section describes fs as "the permissible stress in reinforcement as given below".
Below this, we find references to various maximum values of fs equals various values (such as 24,000) for things like hoop stress, shear stress in rebar, etc. It also lists section 10.6.4 for flexural stress.
In 10.6.4 we find for fs: "The calculated stress, fs, in reinforcment closest to a surface in tension at service loads shall not exceed that given by equations (10-4) and (10-5) and a maximum of 36,000 psi"
The two equations (10-4) and (10-5) are for fs,max. Each equation is a formula and below each there is a statement:
"but need not be less than..." and they give a value such as 17,000 psi.
Now my problem is that as I calculate Sd based on fs, I find I am chasing my tail. As I use smaller bars, or closer spacing, or larger bars, etc. I can't ever catch up to the design moment Sd x U = Sd x Mu.
I am basing Sd on a CALCULATED value of fs at service loads. As I reduce spacing, my fs gets rather small. This kicks up Sd since fs is in the denominator. I never catch up.
Should I be using the fs,max or the 17,000 psi value (as a minimum)? The 17,000 is given as a minimum of fs,max...not as a minimum of fs.
Help!!!!!
Sd = [φ]fy / [γ]fs
Where
[φ] = 0.9 for flexure
fy = 60 ksi for rebar
[γ] = 1.4 (for my fluid load combination 1.4(D+F))
fs = service level stress in the rebar
The section describes fs as "the permissible stress in reinforcement as given below".
Below this, we find references to various maximum values of fs equals various values (such as 24,000) for things like hoop stress, shear stress in rebar, etc. It also lists section 10.6.4 for flexural stress.
In 10.6.4 we find for fs: "The calculated stress, fs, in reinforcment closest to a surface in tension at service loads shall not exceed that given by equations (10-4) and (10-5) and a maximum of 36,000 psi"
The two equations (10-4) and (10-5) are for fs,max. Each equation is a formula and below each there is a statement:
"but need not be less than..." and they give a value such as 17,000 psi.
Now my problem is that as I calculate Sd based on fs, I find I am chasing my tail. As I use smaller bars, or closer spacing, or larger bars, etc. I can't ever catch up to the design moment Sd x U = Sd x Mu.
I am basing Sd on a CALCULATED value of fs at service loads. As I reduce spacing, my fs gets rather small. This kicks up Sd since fs is in the denominator. I never catch up.
Should I be using the fs,max or the 17,000 psi value (as a minimum)? The 17,000 is given as a minimum of fs,max...not as a minimum of fs.
Help!!!!!