ACI 318 Punching Shear - Reinforcement Contribution (Vs)
Jacob-William
3
Hi all,
I'm doing some punching shear checks for a series of columns acting on a 1.0m base slab for a deep underground metro station.
The contribution of stirrups or links is given by S11.4.7.2 in ACI318-11(M), or equivalent 22.6.7.2 in ACI318-19(M) etc.
As the applied shear stress (vu) is taken around the critical perimeter (bo * d), and the concrete contribution to a slabs resistance (vc) is also around this critical perimeter, the shear stress that the stirrups or links must provide is also calculated over the critical area:
ɸvs = vu - ɸvc
ɸVs = ɸvs * (bo * d) {total shear force sitrrups or links needs to provide}
Therefore:
Total Area of Stirrups Required, Av = ɸVs / ɸfyt {where fyt is yield stress of stirrup or link)
Total Area of Stirrups Required, Av = [ɸvs * (bo * d)] / ɸfyt - {Eq. 1}
Up to this point this makes sense to me - and is almost the same as what is specified in the ACI code.
In order to get the above equation I have derived (Eq. 1) to what ACI specifies (Eq. 2) you have to multiply by (s/d), where s is the spacing of longitudinal reinforcement i.e. spacing of perimeter between stirrups or links perpendicular to face of column considered (see below):
Total Area of Stirrups Required, Av = [ɸvs * (bo * d) * s]/ [ɸfyt * d] = [ɸvs * bo * s]/ [ɸfyt] -{Eq. 2 - d terms cancel}
I can rationalize what the use of this factor is trying to do by accounting for the number of 'perimeters' within the critical area d/2 from the face of the column. I.e. if d/2 = 300mm and s = 150mm then you have 2 perimeters within d/2 and therefore you need half the reinforcement so a factor of 0.5 is applied to Av.
However this would require multiplying by a factor of s/0.5d and not a factor of s/d.
I am probably missing something obvious here as I usually design to Eurocodes and ACI is new to me -but I would appreciate if anyone could tell me why a factor of s/d is used instead of s/0.5d?
Thanks in advance!
My understanding is that the provision is considering a single perimeter and that [s/d] is simply counting the number of reinforcement legs likely to be crossing that perimeter.
I think the relationship is derived from Vs = Av*fyt*d/s.
Thank you both for your responses.
@KootK I also think this is considering the amount of reinforcement in the critical area (d/2) from face - however with what I have derived above I still don't see how this equation should have s/d instead of s/0.5d when you consider it from first principles? (i.e. spacing of stirrups or ties within critical spacing from face 0.5?).
It's the amount of reinforcing expected to cross the anticipated shear crack for any punching shear perimeter considered.
Taken as I've explained it above, it couldn't be any more "first principle". The number of stirrups you'll get across a 45 degree crack will be about the depth of the member divided by the spacing of the reinforcing.
I think you need to check your formulation, which seems false.
ɸvs = vu - ɸvc (EQ1)
ɸVs = ɸvs * (bo * d) (EQ2) {total shear force sitrrups or links needs to provide}
For vs = fy(d/s), vu = Vu/b2d, and vc = Vc/b2d; in which b2 = 4sqr(fc')bo, can you demonstrate the validity of EQ1, and how to get to EQ2 from there - in terms of s/d maybe?
If to recall it, Section 11.11 has several types of punching shear reinforcement, depicted in Figures.
Thus, the first stirrup can be no further than d/2 from the first punching zone.
The next punching zone starts at the next stirrup, and then s = d, unless s< d is provided.
Thus, verifying for each outwards perimeter, you get the worst case.
Then if you have overturning, you verify the overturning rotation.