Hello to all,
I am coming to the discussion late too. I have thoroughly enjoyed reading all of your posts. I am glad to see such a lively discussion about this often misunderstood subject. It is exciting to hear so many writing in with fairly accurate, up-to-date information. The word is getting out and that is good news for the industry. I would like to add a perspective that I did not notice in your discussion. We as engineers tend to like the science behind the technologies we use but, sometimes it is difficult to consider the business case. Cost wise the tests per unit can be generally ranked in following order. DC<AC (including 0.1Hz VLF)<TD< on-line PD<off-line PD. However, accuracy and value of the test follows nearly the same ranking. DC<AC<on-line PD<TD<Off-line PD. I have clients ask me all the time, “What test should I use?.” My answer is question. What does a failure of a your cable cost, in outage cost, repair cost, political cost, …. ? If you can give me a cost figure and the application, I will tell you the best test to use. The cost of a failure is not something you are likely to ever hear discussed with IEEE, IEC, ICEA, AEIC, or even little NETA. Let’s keep this simple:
New cable with a potential failure cost <$10k,
I recommend DC megger or a VLF <operating voltage for few seconds to make sure someone didn’t leave the grounds on the other end and turn it on
New cable with a potential failure cost >$25k
Repeat the factory PD test (50/60Hz off-line PD test) to locate any workmanship errors while the installer is on site and require them to repair the system as necessary and learn from their mistakes.
A few (<10) aged cables (>30yrs) with a potential failure cost < $10k ea
I don’t recommend any testing. If you own a TD set you can take a look at them to help get some kind of prioritization information but keep in mind the significant potential for measurement error. Replace cables as funds become available
Many (>20) aged cables (>30yrs) with a potential failure cost of whatever or a few high critical aged cables with a potential failure cost >$25k
Repeat the factory PD test (50/60Hz off-line PD test) to locate any insulation defects and use the information to develop a repair/ replace strategy. .
I would like to review some of the data we have collected over last decade:
I agree that the DC withstand test is not good for aged PE cable systems
I agree that the DC withstand test can not detect most defects in extruded systems (detects approx. less then 1% of defects)
Our client’s experience indicates at the AC (including 0.1Hz) withstand test can not detect most defects in new extruded systems (detects up to approx. 3x more than DC, less than 3% of defect)
Our client’s experience indicates that a 0.1Hz AC withstand test will typically fail any where from 10 to 40% of critically aged xlpe systems. An in some cases the cable systems have higher failure rate after the testing.
Cable and accessory manufacturers use the PD test as the final insulation quality check for their products
I agree that TD is a good insulation property test but, it can not detect where the losses are coming from.
Recent TD studies show that most of the losses measured by typical field TD tests come from termination and splices which can have 10, 100, 1000 times more losses than cable insulation and still perform reliability.
Almost all TD tests performed in the field today do not employ guard circuits at the terminations and thus are susceptible to substantial leakage measurement error.
An on-line PD test detects approx. up to 3% of defect in cable systems.
An off-line PD test detects on the order of 99% of defect in cable systems if…. administered properly. TDR mapping, sensitivity assessment, pC calibration, and measure cable response at the IEEE thresholds.
A10jp, as far as the DC test, I am sure you can cover your political basis with a DC test but, don’t count on it to assure reliability. The test voltage values are nearly inconsequential. I do recommend an IR reading as you go up to operating stress level to see if there is a tip-up in the curve. Some times you get lucky and the defect has enough conduction to show up even if it does not fail.
Cheers,
Benjamin Lanz
Past Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants