don01, Thanks for the response! Since I had posted the question, we dug further into our system, and found that the grounding was a definate problem. One interesting point, is that we interface control signals with another plant that supplies us with steam, oxygen and nitrogen. We have both fibre optic and electronic signals going back and forth. Of course the fibre signals are no problem, but the wiring for the electronic signals passes through a junction box at the fence between the plants. What we found was the shields for these signals were tied together in this JB. Essentially what we had was a big ground loop between the two plants. Although this wasn't the only ground problem we found, it is a point to remember when interfacing between DCS systems.
We are running Fox IA, with Rosemount 3051 series transmitters. We were seeing up to 150mVp-p of AC on the 24VDC.