ABB-REG670 voltage protection(60) and fuse failure(RFUF)

Status
Not open for further replies.

odlanor

Electrical
Jun 28, 2009
689
Does anyone knows the difference in the of application of Voltage differential protection (PTOV, 60) and Fuse failure supervision (RFUF)?
It seems samething.
 
Replies continue below

Recommended for you

Hi odlanor.
Its not same, differnt pinciple of operation and not only for REG670
function 60 is volatge phase differntial protection and two VT on the bus/line are needed.
FFS is voltage/curent function, operated on the U2/I2 or U0/IO or both of them principal.
Hope that help.
 
slavag
I am talking about difference in the application, not principle of operation.
 
Sorry, my mistake.
Yep, application is a same.
 
slavag . that's the problem.
REG670- function FFS block functions 40, 21, 27, etc
REG670-function 60 does not.

 
Hi.
its free programmable in the PCM600
depend on your standards
 
Document ID: 1MRK502016-UEN
Issued: December 2007
Revision: B
IED product version: 1.1
 
odlanor,
Can't you just set it up to block the functions you want under signal matrix?
 
JG2828
I'm not familiar with the REG670 to answer you.
I always saw 60 function blocking those functions 21.40, ...
I wonder what is the advantage of using 60 or FFS to block functions 40, 21, 27.
 
Hi.
No advantages, its used, when you not have a second VT.
ActualLy, 60 is best solution.
Of course possible do it (if it prepared) in the single matrix.
 
You cannot block the function directly with the signal matrix. You can definitely do it using PCM600.
 