SmithJ
Structural
- Apr 11, 2003
- 72
I have a situation here.
We designed a riding arena structure and asked that the erector put up the steel using turn-of-the nut method since all the bolts were high strength A490 Bolts. The Erector does not indicate a problem with this and goes ahead to erect the building. Fast forward a few months, trying to get occupancy and the building department says they need a bolt inspection. Bolt inspector goes on site and says that he can't sign off on turn-of-the nut because he wasn't present during erection and can't see the chalk marks.
The inspector suggested that he would sign off if we state that snug tight is adequate on this project. I refused and said we can't recommend anything contrary to the code (Code clearly states that A490 bolts can't be snug tightened).
Any ideas on how best to resolve this? I went through the RCSC spec and it seems that Table 4.1 gives minimum fastener tension for varying bolt sizes. Is it okay to say that these minimum tensions meet the preloading requirements of turn-of-the nut method?
Any help is much appreciated.
Thanks,
JS.
We designed a riding arena structure and asked that the erector put up the steel using turn-of-the nut method since all the bolts were high strength A490 Bolts. The Erector does not indicate a problem with this and goes ahead to erect the building. Fast forward a few months, trying to get occupancy and the building department says they need a bolt inspection. Bolt inspector goes on site and says that he can't sign off on turn-of-the nut because he wasn't present during erection and can't see the chalk marks.
The inspector suggested that he would sign off if we state that snug tight is adequate on this project. I refused and said we can't recommend anything contrary to the code (Code clearly states that A490 bolts can't be snug tightened).
Any ideas on how best to resolve this? I went through the RCSC spec and it seems that Table 4.1 gives minimum fastener tension for varying bolt sizes. Is it okay to say that these minimum tensions meet the preloading requirements of turn-of-the nut method?
Any help is much appreciated.
Thanks,
JS.