aggman
Structural
- Jun 9, 2003
- 253
We have designed several material processing plants over the past few years in Florida and lower Alabama. As a rule, even if ground water is not an issue, we have always designed the foundations for buoyancy in the hurricane regions. Our justification is that during a hurricane there is always mass flooding to go along with it and the foundations will likely be submerged under water during the storm. I recently had another firm looking at a design we had done and they were questioning the inclusion of buoyancy for the foundation design when the water-table was four - six feet below the bottom of the foundations. We explained our reasoning and he felt that we were just killing it to be conservative. In the end we were signing off on the design so we stuck to our guns, but I am wondering what other opinions are on this. Thanks for your input.