Hello.
I would like add several points.
Standard solution in this case is 50/51, but don't forget:
On the second side( w/o generation) we must install
directional overcurrent 67 with time delay about 0.2-0.5sec.
If we use 67N as back-up protection, we also must install on other side 67N with reverse direction ( time setting lower then 67N on generation side).
Please see attached scheme:
Regards.
Slava