niilaryea
Electrical
- Aug 8, 2011
- 6
The restrict earth fault on my unit transformer 169MVA 161kv has been operating any time there is fault in the Grid. On one of the disturbance records , it was observed the polarity of the High side CT and neutral CT were the same. Am tempted to reverse the polarity of the Neutral CT. I would appreciate you advice on this.I have have upload the the disturbance and one line.