GSI1 – you wrote:
As for ac hipot testers are not destructive keep in mind when the equipment under test fails their will be an arc. Any arc through the insulation is destructive and I would never put it back in service. If you would then I am glade I don’t have to work with you. [B/]
In my opinion that comment has no basis since I have said nothing about ac hi-pot testing (IEEE95 is the standard for dc hipot testing), and I have never said I would put a machine back in service following a failure of an ac or dc hi-pot. I am happy to discuss it further, but I hope we can discuss it and even disagree without making it personal.
Here is my view:
There are at least two dc tests available:
#1 - The insulation resistance test/polarization index (IR/PI) per IEEE43-2000 at 500vdc for 460 motors, 2500vdc for 4kv motors, and 10kv for 13.2kv motors.
#2 – The dc hi-potential test per IEEE95-1977, where voltage may be increased over time in a variety of fashions, but to levels far above peak line-to-ground voltage.
There is no disagreement among anyone I know of that #2 = dc hi-pot will identify more problems than #1 = insulation resitance test.
I think there is also no disagreement among anyone I know of that testing by # 2 = dc hi-pot will cause more motors to fail (become unuseable requiring rewind) than #1 = insulation resistance test. You yourself have said that a motor should not be used after it fails a hi-pot and I agree.
One unknown and controversial question: how bad are the motors which fail the dc hi-pot? ie long would that motor that failed the dc hi-potential test have lasted if you hadn’t tested it. or put another way: how many motors will fail that were really “good” in terms of their ability to operate for many more years.
Given the above considerations, there are some situations where the economics will clearly dictate that the dc hi-pot is required and some situations will dictate that the dc hi-pot is clearly not appropriate. If you have a critical motor whose failure will cost 1000 times as much as the cost of a motor rewind AND you have a spare motor available, the argument for performing a dc hi-pot is pretty strong. But there are many situations where dc hi-pot is not a good idea:
1 – cost of rewind is much more than cost to production. Let’s say you have 3 installed motors, any one of which can startup automatically to support production. Cost of motor failure to production is zero. Cost of rewind is large. It does not make sense to hi-pot test these motors to a point that might cause failure. Let them run to failure if necessary. But also check insulation resistance periodically when motor is down for air-filter and lubrication maintenance soo you can take corrective actions (clearning/drying etc) to avoid the cost of a failure/rewind.
2 – You have a motor which is critical to production but you have no spare. It will only be available for testing for a short time before it must be returned to service. You can confidently do an insulation resistance test without fear of jeaparding production. If you see a clear indication of a problem then you may be able to initiate corrective action justifying the purchase of a spare motor if required. If you apply a dc hi-pot at the voltages you describe you might damage that motor to the point that a rewind is required. In case of a 13.2kv motor the time to rewind can be at least a month even when you expedit the rewind shop (special coils). Productoin will be disrupted and I don’t think the plant manager will be happy to find out that a motor tester has caused it.
3 – You have a motor though underground vaults, through XLPE cables which sometimes get wet. This medium-voltage motor requires taped connections due to the tight clearances within the terminal box. Removal and resinstallation of taped connections will require several hours, and also raises questions about the integrity of the joint after reassembled. You can easily do a quick check of the motor/cable from the switchgear. If you apply a high-voltage dc test at 2*VLL+1 to the motor though an XLPE cable which has absorbed moisture, you will likely degrade the cable and possibly fail it.
To you question: why even bother doing an insulation resistance test alone (without hi-pot)?
1 – You have a motor that is wet (maybe you don’t know that). Careful analysis of the insulation resistance/polarization index may identify that without damaging the winding. Then the motor can be dried out (space heaters repaired or whatever) before energizing without damaging the motor. If you had applied a dc hi-pot to a wet motor at the voltages you describe you might damage that motor to the point that a rewind is required.
2 – You have a motor whose windings are contaminated with oil and dirt (you may not know it). Careful analysis of the insulation resistance/polarization index may identify that without damaging the winding. Then the motor can be cleaned. If you apply a dc hi-pot at the voltages you describe you might damage that motor to the point that a rewind is required.
I agree the insulation resistance test is not perfect and can sometimes miss moisture, contamination, and other winding degradation. There is a lot that can be said about methods for trending, temperature correction, consideration of humidity etc. Neither is the hi-pot test perfect in detecting insulation problems…. certainly neither of these tests will detect turn insulation problems. That will require a separate potentially-destructive test – the surge test.