When smaller equipment from a 50 Hz system is to be used on a 60 Hz system, or 60 Hz equipment for 50 Hz use, any change in core losses is generally ignored. For motors the change in load characteristics is important especially for unit pumps and fans.
The results are generally:
Maximum rated current; the same.
Maximum rated voltage; changes in the ratio of Hz2/Hz1 For 60Hz to 50 Hz, 50/60
Maximum rated KVA or HP; changes in the ratio of Hz2/Hz1 For 60Hz to 50 Hz, 50/60
Speed for motors; changes in the ratio of Hz2/Hz1 For 60Hz to 50 Hz, 50/60
A dual rating of 110V, 50Hz/120V, 60Hz is common on a lot of small control equipment. eg; Contactor coils, some control transformers, small motors such as shaded pole or verry small synchronous motors.
I do not intend to contradict ScottyUK in any way. I generally work on small equipment, about 1 MW or less. Scotty works on equipment in the MW range. Size matters and effects that are ignored or not even noticed on small equipment become serious issues on the big stuff.
Bill
--------------------
"Why not the best?"
Jimmy Carter