That all depends. Depends on the sheath, its thickness, the exposure environment, service maintenance, water ingress, construction techniques...and others.
In the mid-70's was when extruded sheaths was introduced into the unbonded PT industry - actually it was patented by Lang in 1972 . Prior to extruded sheaths, you had kraft-paper, heat-sealed and "stuffed" sheath systems for strand. Both grease and wax compounds were used, and neither was to any particular quality standard.
I have seen strand tendons with no grease and in fine corrosion-free condition due to the lack of presence of water on the concrete structure and within the tendons.
But I have also seen tendons with grease voids, punctured sheaths, corroded end-anchorage pockets, zero concrete cover, with substantial corrosion.
You cannot answer you question with any practical significance. If you are in doubt of the corrosion protection, or the conditon of the tendons, do a Condition Survey of the strcuture. Check for water ingress through cracks, CJ's etc. Be aware that corrosion damage to unbonded PT structures often is not visible from external observations - ie won't see spalls as you will for rebar corrosoion, probably will not see failed tendons via loops or strands shooting from slab edges. If you suspect corrosion damage and it is not visible, I advise some selective invasive probing - chip and remove concrete cover and expose the tendons and selected locations. Bit like finding a needle in a hay stack, but is a start. Check out live end grout pockets too. You may see signs of grease stains on the slab soffits too co-inciding with crack locations.
There are some good ACI documents on this subject that you may wish to check out. Let me now if you have access to ACI document and I will list them for you.
Current monostrand tendons with extruded sheaths and greased strands are manufactured to significantly better quality than older systems.
HTH