Ground Potential Rise (GPR) = Ig * Rg
For 500 kVA, 13800-480/277V, Dyn effectively grounded at Z=5%, Ig = 12kA taking an infinite primary source.
The contractors are providing a loop grounding grid buried around the building and aiming to obtain 5 ohms maximum.
Based on 5 ohms, GPR = 12,000 * 5 = 60 kV
This is quite very high.
IEEE 80 provides formula to calculate the tolerable touch and step potentials....however, the design GPR is very high. When asked, the contractor informed us that it has been their practice to get Rg = 5 ohms and call it a day.
The Code is even specifying for a higher one ( I think 25 ohms).
Is this a valid design application? Is the GPR neglected (regardless of Ig) in the building design?