zaes73 -
I would seriously question the testing lab about the reporting AND the testing procedures. The results are so low and bizzare, there must be some very obvious reason.
Could non-standard shapes have been tested or could you be looking at a prism report? While 5 days is not a factor for block, it is not reasonable and probably not even verifiable and indicates an unusual practice. For a prism, it could be an indicator, if it was possible to handle a prism without damage at 5 days.
In the 30 years I was was involved in the manufacture of concrete masonry units we were never able to make a block that weak. The use of non-loadbearing block has ceased because the manufacturing process makes the manufacture and inventorying of non-bearing units uneconomical and impractical. The biggest compliants in the industry is that the strength requirement (1900 psi) is rediculously low and actually dates back to the 1920's.
I have made block out of sand and rice husks/hulls and out of sand and wood chips/sawdust that were over 2000 psi, which is far more than you are seeing.
ASTM C90 requires a compressive strength of 1900 psi based on the net area. About 20 years ago, the strength requirement was based on the gross area, which was really not a measure of the strength of the concrete. ASTM C140 is a testing procedure and not product standard and as such, an age requirement has never been considered and block are not identified by manufacturing dates, except in the case of optional identification (usually on the pallet) for architectural units where the block are made in special colors for a specific project.
There is no requirement for the age in the ASTM C90 standard since it is a performance requirement based on the properties when the units are used. The type of concrete in a concrete block is a "zero slump" mix and not a wet cast concrete with curing in the plant. Typically, this type of concrete will be closer to 90% when used. The cheapest and easiest way to increase the strength of a concrete masonry unit is to add extra water to this type of mix, but contractors would not buy the block.
If a sound unit is selected for testing, it is very difficult to get a low value. As an example, capping with gypsum board scraps or plywood scraps only decreases the indicated compressive strength by 10-15%. In the case of very high strength block (4000 psi to 8000 psi), some testing labs do not have adequate platen thicknesses (too much deflection/bending) to accurately test these units. This is because the typical cylinder testing is not adeqaute without swapping out the platens. For lower strength units, this would not be a factor.
I would suggest also contacting the testing lab to look at the history for that supplier for clues.Many jurisdictions require independant testing for licensing and certification of block producers.
As you point out, the strength of 452 psi does not seem correct and does not comply with any standard.
Dick