Jul 28, 2010 #1 SteveMort Structural Joined Oct 30, 2006 Messages 43 Location US I have an existing building with 48LA18 joists at 8'-0" spanning 88'-0". Does anyone have load capacity tables for this joist? circa 1963.
I have an existing building with 48LA18 joists at 8'-0" spanning 88'-0". Does anyone have load capacity tables for this joist? circa 1963.
Jul 28, 2010 #2 MiketheEngineer Structural Joined Sep 7, 2005 Messages 4,654 Location US My copy of the 75 year Steel Joist Manual shows: Max end reaction: 23,735 lbs max load: 518 plf Weighs: 61 plf Go to their website: steeljoist.org for details Upvote 0 Downvote
My copy of the 75 year Steel Joist Manual shows: Max end reaction: 23,735 lbs max load: 518 plf Weighs: 61 plf Go to their website: steeljoist.org for details
Jul 28, 2010 Thread starter #3 SteveMort Structural Joined Oct 30, 2006 Messages 43 Location US That's a big help . . . thanks Mike. Upvote 0 Downvote