Dear Mr. HamidEle,
1. Please tell us more details:
a) Motor 460V is 3phase , kW rating. Winding is in "star" or "delta" formation? What was the (trip voltage) recorded?
2. Did you carry out the [insulation resistance test] at (500Vdc or 1000Vdc) with respect to earth/frame
a) (if it is wound in star, with six terminals accessible), of each individual winding ? What are the (three) readings?
b) (if it is wound in delta), only one measurement is required. What is the reading?
3. In general, a motor rated 460Vac with insulation resistance to earth >2M Ohm would be acceptable to proceed on with the next stage "high voltage" test. The test voltage may be dc or ac.
4. If your test set has a [current trip] setting, set it to [maximum] (temperately) . Attention: see 5 below.
5. Increase the test voltage slowly and smoothly. Observe the leakage current (if the test set is equipped with one). Otherwise, observe the volt meter. It should be smoothly increasing without fluctuation, up to the final test voltage and maintained for the duration. Attention: take note the voltage reading when the volt meter (starts to fluctuate) and when it [trips}.
6. For high voltage test, the value of the [withstand voltage (in kV) and the duration (in s)] are the governing factors. That is why some simple HV test sets are not equipped with the leakage current meter.
7. If [insulation resistance] is in order but failed on [high voltage dielectric test], look out factors that are affecting the "creepage" and the "clearance" distances or cracks in the insulation material.
Che Kuan Yau (Singapore)