Dear Mr. HamidEle (Electrical)(OP)18 Mar 20 03:02
1. " FYI, the vendor came back and recommended to use 500v to Meggaer 460v motor as it is not ...."
Agreed.
Reference: (Megger an instrument manufacturer) states that commonly used test voltage for routine maintenance for equipment rating 440-550Vac , the test voltage is 500-1000Vdc.
2. Insulation resistance value taken with 1000Vdc may differ from the value taken with 500Vdc with the same duration and temperature. They do not indicate any defect if both readings are above the generally minimum acceptable resistance value.
3. In practice, a 460Vac motor [should be able],(without any ill effect) to be tested at !000Vdc.
4. Although testing a 460Vac motor at 500Vdc seems to be low, while testing it at 1000Vdc seems to be better, but NOT necessary.
Che Kuan Yau (Singapore)