4160V breakers have the protection devices physically separate from the breaker itself. For routine testing, the protective relays would be tested with test current representative of what flows in the secondary of the associated current transformers.
Breakers at 600V and below generally have all the protective devices contained on the breaker itself. The most thorough test of those devices is to inject primary current equivalent to what actually flows through the breaker during an overload or fault (except that the test current is driven by a much lower voltage level than the "real life" operating voltage).