3" DIA x 6" CONCRETE TEST CYLINDERS
PT999
150
I am seeing these smaller concrete test cylinders being used to mold concrete for compressive strength vs the traditional 6" dia x 12" high test cylinder molds
Is this permitted by ACI
4x8's are now permitted by aci and ibc. you should read the documentation though since it requires more specimens and possibly different equipment.
I would guess you are seeing 4"x8" cylinders rather than the 3"x6" in the thread title. As msucog pointed out, ACI standard strength acceptance is based on 2 - 6"x12" cylinders or 3 - 4"x8" cylinders at 28-days. No matter what, you are still limited to 3x the maximum aggregate size of the aggregate in the concrete per ASTM C 31, and the consolidation procedure is 2-lifts with a 3/8" diameter rod. The 4"x8" cylinders can only be used for concrete containing aggregates up to 1 1/4" maximum size.
Greg