Suggestion: The previous posting is continued since there are more UPS architectures that may be found useful, namely,
Different UPS architectures are included in Reference:
1. IEEE Std 241-1990 IEEE Recommended Practice for Electric Power Systems in Commercial Buildings", (Gray Book)
Figure 39 "Single-Module UPS System" on Page 198
Figure 40 "Parallel Capacity UPS System" on Page 199
Figure 41 "Parallel Redundant UPS System" on Page 199
All above UPSs are good for powering critical loads
Figure 42 "Dual Redundant UPS System" on Page 200
(Good for computers.)
Figure 43 "Isolated Redundant UPS System" on Page 201
(Good for critical loads.)
Figure 44 "Parallel Tandem UPS System" on Page 202
Figure 45 "Hot Tied Bus UPS System" on Page 203
Figure 46 "Super-Redundant Parallel System - Hot Tied Bus UPS System"
Figure 47 "Uninterruptible Power Supply with Dual Utility Sources and Static Transfer Switches"
etc. The above represents a good start to UPS architectures and configurations.