I have a vacuum conveyor for pellets of plastic raw material and it uses a 3-phase motor, 5.2 amps (nominal) and it runs on 480V. Originaly, there were 3 x 6-amps fuses on it. Then, it started blowing fuses with no apparent reason. I called the manufacturer and I have been told to replace the fuses for 10-amps time-delay fuses. The blower is running with around 6 amps on load, and its starting current goes up to 25 amps sometimes (normally goes to 22 amps). Its cycle lasts only 30 seconds every 2 or 3 minutes, so it starts and stops all day long. The body temperature went to 165F today and it burnt 6 10-amp fuses just today. Control pannel looks ok, it works fine. Voltage is around 475V.
Does anybody have any idea?
Does anybody have any idea?