3 Phase Motor Amp Draw

Status
Not open for further replies.

KCOhmite

Electrical
Joined
Dec 20, 2006
Messages
3
Location
US
If I have a piece of equipment (electric oven used for burn-in) that states on it's power label the following:

Power: 480V 60Hz 3phase
Line Current: (amps per phase) 33.0

Does that mean it needs 99.0 amps (33.0 x 3 phases) or 11.0 amps (33.0 / 3)?

I think it is 99.0 amps.
 
It means that it needs 33 amps on each phase.

Add the three currents together and you magically get zero amps.
 
Cool - that's what I told my coworker. Another coworker was thinking it was 33A total.

Thanks!
 
I am not EE, but I asked one co-worker EE and he says the amp drwa is 33 amps.
 
It is 33 amps Total. Phase 1 current draw 33 amps, phase 2 current draw 33 amps, phase 3 current draw 33 amps = a Total of 33 amps MAX! Not 99 amps Total. Three phase 40 amp breaker or fuse for power distribution.
 