3 Phase Injection Set 1

Status
Not open for further replies.

Sharpie8

Electrical
Joined
Aug 3, 2013
Messages
11
Location
AU
Hi, is anyone aware of commercially available 3 phase injection sets for primary injection (e.g. BBP stability). Ideally currents into several kA would be required.
Thanks.
 
Low-voltage rental generator. Disconnect the AVR and control the field manually using a lab power supply. If you're using it as a single-phase source then disconnect or disable the negative sequence protection. Possibly easier to forget to mention to the rental company what you're going to do. You can get up to about 4kA from a 2.5MVA set, perhaps a bit more for a short period of time.
 