I am trying to size a circuit breaker for a 3 phase motor given it's power consumption. Note that I am not sizing a thermal overload.
Here goes:
Working with 480 VAC Delta and a motor rated at 3.5kW.
If the total power of the motor is 3500 Watts, than each winding is supplying 1/3 of that = 1167 Watts per winding.
At 480 VAC across each winding, there is a Line current of 1167/480 = 2.43 Amps.
Assuming an inrush current at a safe 10 times nominal, I would need a 25 Amp 3 phase breaker.
How close am I to the truth? Thanks for your help and corrections.