Hi,
I refer to the drawing uploaded on the following site:
Someone wants to put a 3P breaker at the transformer side, and 4P breaker at the generator side.
I say 4P breakers on Generator and on Transformer sides, because whatever reason for having a 4P on one source would probably be valid for the second source as well.
Notably, if the phases are not balanced and current flows in the neutral, then: if 3P breaker is used at the transformer, current will close the loop though this unbroken neutral, particularly if the connection between earth and neutral is lost for some reason.
Could you please tell me what do you think about this?