3 Generator Load Sharing Question

Status
Not open for further replies.

ThePunisher

Electrical
Joined
Nov 7, 2009
Messages
384
Location
CA
HI all,

In one the facilities of our system, I can help notice this and took a photo.

All three generators are running under-loaded and the power factor is 1.09 of one and around 0.50~0.51 on the other two. If these generators are running in load sharing mode, why are their kvars or kVA not equal?

This is for my educational purpose only.

Regards,
 
 https://files.engineering.com/getfile.aspx?folder=556534b1-6e45-496e-a01e-14284219b2cc&file=Generator_Control_HMI.jpg
The fist approach for this is taking DG3 offline and check the offline voltage and compare this value with the data sheet. This voltage check should be done with a multimeter with a least 2 decimal place.

IF you can post a picture of the AVR and generator controller schematic.

Regards,
JS.
 
redlinej,

I will try to get it for you if I can and post it here later.
 