For tall wall 2x6 studs, is consideration ever given for the 7/16" OSB sheathing (outside face) and 1/2" GB (inside face) for resisting bending from out-of-plane C&C wind loads? I have a residential client who is building a 52'Wx90'Lx16'H garage/shop. 35 psf roof balanced snow, trusses at 24" o.c. Stud height is 15'-7_1/2". I modeled the stud in WoodWorks using a 2x6 SFP No.1/2. It does not satisfy the combined axial compression and side load bending criteria of AWC NDS equation 3.9-3. (see attached WoodWorks output). Obviously there are a few options: tighter 12" o.c. stud spacing, higher grade lumber (or LSL studs), 2x8 studs, or double 2x6 studs at 24" o.c. aligned with the roof trusses. I'm thinking that the column stability factor, Cp, of the stud should be higher. Any input is appreciated.