I have a wacky idea that needs vetting.
I've inherited a 250 mm, one way concrete slab that spans 9 m. Deflection is a problem. I'd love to thicken or post-tension it but neither of those options is possible. Instead, I'm considering packing the slab full of continuous tension and compression steel (2-15M bundled at 150 mm o/c). I intend to design the slab, for both strength and stiffness, as though it were a steel only section comprised of the tension and compression steel acting compositely (no concrete). My thinking is as follows:
1) If I use the same amount of top and bottom steel, there ought not be any curvature induced by shrinkage.
2) When creep starts to kick in, the concrete should shed it's compressive load to the compression steel.
Some concerns that I have are:
1) Usually creep is conceived of as a compressive stain. Is there a shear component to it that would invalidate my assumption of near perfect composite action between the tension and compression steel?
2) If I'm using the top bars in compression, do I need to provide ties to prevent them from buckling? That would probably be a deal breaker. If I remember correctly, there's a provision for compression members somewhere in ACI that lets you omit compression steel ties when the area of reinforcement is <1%. I'm not sure how to apply that in my case however. I've got about 1.6% reinforcing in both the top and bottom of the slab (3.2% over the whole section).
Thanks for your help.
KootK
I've inherited a 250 mm, one way concrete slab that spans 9 m. Deflection is a problem. I'd love to thicken or post-tension it but neither of those options is possible. Instead, I'm considering packing the slab full of continuous tension and compression steel (2-15M bundled at 150 mm o/c). I intend to design the slab, for both strength and stiffness, as though it were a steel only section comprised of the tension and compression steel acting compositely (no concrete). My thinking is as follows:
1) If I use the same amount of top and bottom steel, there ought not be any curvature induced by shrinkage.
2) When creep starts to kick in, the concrete should shed it's compressive load to the compression steel.
Some concerns that I have are:
1) Usually creep is conceived of as a compressive stain. Is there a shear component to it that would invalidate my assumption of near perfect composite action between the tension and compression steel?
2) If I'm using the top bars in compression, do I need to provide ties to prevent them from buckling? That would probably be a deal breaker. If I remember correctly, there's a provision for compression members somewhere in ACI that lets you omit compression steel ties when the area of reinforcement is <1%. I'm not sure how to apply that in my case however. I've got about 1.6% reinforcing in both the top and bottom of the slab (3.2% over the whole section).
Thanks for your help.