50 Hz/60 Hz operations have been discussed before - The FAQ sheets in this forum were useful. Thank you. I also reviewed all threads going back to January this year, but saw nothing exactly like this problem.
Nameplate Data:
Frame 449TS, rated 460 volts @ 272 amp.
NEMA 3, 3 phase TE 8404 (B404 ?)
250 Hp 60 Hz/1780 rpm
Westinghouse brand
Background. This question was asked in the pump forum - and several good points brought, solved, and resolved. Several readers there recommended that the motor issues be addressed here:
I have a large portable US-built oil filter system that (now) can only run properly in Europe's 50 by renting an temporary 60 Hz generator and fuel tank.
Obviously, renting the generator is too expensive nowadays (several tens of thousands of Euro's), hurts sales and increases costs and setup time (crane time, truck rental, space, etc.)
Boss wants to use the current motor at 50 Hz instead.
Temporary Generator output now, while the pump is running in a "standard flush configuration:
464/458/456 volts on the three phases
214/225/220 amps
.89 pf using 149 - 152 Kw.
If I run at 1450 rpm (nominal 1500 for 50 Hz) instead of 1800 rpm from the generator's 60 Hz, my flow is too small. (Pump is a ITT 10x12x14 3405 type with a max impeller, flow spec is 4200 gpm minimum.)
if I change pumps (and use the same motor at but at the European 380-420 volts and 50Hz ) to the larger 10x12x17 casing, It appears I can regain the flow and keep in the same 3405/3410 "family" so my baseplate still fits.
Filter, suction and discharge piping would stay the same, so I expect the resistance to be the same.
The new casing moves the pump suction and discharge lower by 1 inch - but physically I can shim up motor and pump casing back to old height. Left right distance can be compensated for.
1) Running time for the flushes is 120 to 160 hours, but the pump will only be used for a few weeks every year.
2) A a lower speed and lower voltage, the motor heats up more. Can I calculate this extra heat or even estimate it?
3) At a lower speed there is more current: Is the nameplate rating of 272 threatened? Actual auxiliary voltage on the power plant's system panels varies a little, but is displayed as 400 VAC, 388 VAC, and 390 VAC.
4) Any other problems anybody can foresee? Softstart motor controller manual says it is rated for 50 Hz ops after a switch is changed on the control box.
Nameplate Data:
Frame 449TS, rated 460 volts @ 272 amp.
NEMA 3, 3 phase TE 8404 (B404 ?)
250 Hp 60 Hz/1780 rpm
Westinghouse brand
Background. This question was asked in the pump forum - and several good points brought, solved, and resolved. Several readers there recommended that the motor issues be addressed here:
I have a large portable US-built oil filter system that (now) can only run properly in Europe's 50 by renting an temporary 60 Hz generator and fuel tank.
Obviously, renting the generator is too expensive nowadays (several tens of thousands of Euro's), hurts sales and increases costs and setup time (crane time, truck rental, space, etc.)
Boss wants to use the current motor at 50 Hz instead.
Temporary Generator output now, while the pump is running in a "standard flush configuration:
464/458/456 volts on the three phases
214/225/220 amps
.89 pf using 149 - 152 Kw.
If I run at 1450 rpm (nominal 1500 for 50 Hz) instead of 1800 rpm from the generator's 60 Hz, my flow is too small. (Pump is a ITT 10x12x14 3405 type with a max impeller, flow spec is 4200 gpm minimum.)
if I change pumps (and use the same motor at but at the European 380-420 volts and 50Hz ) to the larger 10x12x17 casing, It appears I can regain the flow and keep in the same 3405/3410 "family" so my baseplate still fits.
Filter, suction and discharge piping would stay the same, so I expect the resistance to be the same.
The new casing moves the pump suction and discharge lower by 1 inch - but physically I can shim up motor and pump casing back to old height. Left right distance can be compensated for.
1) Running time for the flushes is 120 to 160 hours, but the pump will only be used for a few weeks every year.
2) A a lower speed and lower voltage, the motor heats up more. Can I calculate this extra heat or even estimate it?
3) At a lower speed there is more current: Is the nameplate rating of 272 threatened? Actual auxiliary voltage on the power plant's system panels varies a little, but is displayed as 400 VAC, 388 VAC, and 390 VAC.
4) Any other problems anybody can foresee? Softstart motor controller manual says it is rated for 50 Hz ops after a switch is changed on the control box.