I am aware that some areas, primarily in the western US, both irrigation and downhole pumping are using single phase source to a VFD acting as a phase converter then the 3 phase pump motor. But I'm having a problem seeing the cost justification in this scheme. It seems to be mainly 5 to 70hp. But once the drive is oversized by 75 to 100%, then the cable is oversized likewise, then you compensate for the horrendous single phase current distortion with an expensive filter, can there really be that much savings in running the 3rd wire. Especially when with 3 phase the wire is smaller? Help me4 under stand the cost justification of such a system.
Neil