Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

1997 UBC Wind Loads for Components

Status
Not open for further replies.

Berniedog

Structural
Dec 19, 2005
200
Has anyone ever compared the ASCE 7-02 component wind loads to the 1997 UBC wind loads for components? We started reviewing shop drawings for a project for claddding and girts for a transfer tower using the ASCE spec. and then found out we had to use the UBC. My calcs. show an increase in wind load of 50%. They are saying I am wrong but at this time won't review my calculations. It is costing the fabricator money.

It is exposure C at 105' high, 90 mph, 68 sf. area of cladding for the girt loading.

Thanks
 
Replies continue below

Recommended for you

Here's what I get:

UBC 97
Wind - 90 mph
Exp C
Height - 105'
Area 68 sf


qs = 20.8 psf

Wall Elements not in areas of discontinuity - enclosed and unenclosed buildings
Area = 10 sf: +/- 40.6 psf
Area = 100 sf: +/- 30.4 psf

Wall Elements not in areas of discontinuity - partially enclosed buildings
Area = 10 sf: - 54.1 psf
Area = 100 sf: - 43.9 psf

Wall Elements in areas of discontinuity
Area = 10 sf: + 40.6 psf and -50.7 psf
Area = 100 sf: + 30.4 psf and -40.6 psf

 
Make sure you are using the correct/converted wind speeds between the two methods... then I believe they should be fairly close for the resultant pressures (not 50% difference).

UBC uses 'fastest mile' wind speed
ASCE uses '3 second gust' wind speed

90mph(3 second gust) converts to approximately a 76mph(fastest mile) wind speed.
or
90mph(fastest mile) converts to approximately a 105mph(3 second gust) wind speed.
 
JAE WAMRE Thanks. Can you take a look at the following:

P=Ce*Cq*qs*Iw
Ce=1.62
Iw=1.15
Qs=20.8
Wall Elements not in areas of discontinuity - enclosed and unenclosed buildings
A=68sf. Cq:1.01
P=39.1 psf- inward & outward

Roof Elements not in areas of discontinuity - enclosed and unenclosed buildings
Cq=1.11
P=43.04 outward

Wall Elements in areas of discontinuity
Cq=1.01 inward
Cq=1.31 outward

p=39.1 psf inward
p= 50.8 psf outward

Roof Elements in areas of discontinuity - enclosed and unenclosed buildings
Cq=1.78

P=69.0 psf outward
 