Krusher
Although I know of no AFD that contains a low temp detector, it would be a good idea. In jOmega's post above he made a typo on the temperature conversion; 0C = 32F, not 0F. There is a reason why NO drive can be rated for OPERATION below freezing. Are you aware that by energizing that drive at 5F you are risking severe damage to the capacitors? If the electrolyte in the cap core freezes, it creates a dead short. The caps will explode, and I have witnessed it as a particularly violent event, sending the AFD cover sailing off about 100 feet! You don't even need to give the drive a run command, it happens when you just put power on the line terminals.
Come to think of it, one thing I know about AB 1336 AFDs is that on larger sizes they use an SCR front end rectifier. They use it to ramp initial applied voltage into the DC bus so as to not stress the caps (as opposed to a charging resistor as many others use). With this method, it is possible that some smart engineer at AB added a low temp cut off switch to the SCR firing board so that you cannot energize the DC bus below freezing. Great idea if they did. I have found that several AB service techs were not even aware that the 1336's had an SCR front end, they just assumed it was a diode bridge. I had to learn it from the factory people once when I had a failure in the field. That could explain why your tech was not aware of any low temp device (if any).
Generally, if you need to operate a drive at below freezing I recommend the following. Go to a refrigeration parts distributor at pick up a "freeze-stat". This is a thermostat which operates for freezers where the contact CLOSES on temperature rise. Find one with a range that works at around 40F, and place the sensor bulb near the top of the AFD heat sinks. Wire it into a contactor for line power and add a heater so that when power is applied, only the heater is energized until the freeze-stat bulb sees 40F. When warm enough, the freeze-stat closes and line power is applied to the the drive. If your AB drive indeed has a similar function built in, just add the heater and make everyone aware that it will take some time before being able to run.
Subvert the dominant paradigm... Think first, then act!