urielcdc: Sorry for the delay in response, I have been out of the office. Unless you are working in a location that has adopted a code that refers to the older ASCE requirements, it doesn't really matter what ASCE 7-95 says, other than the historical evolution of the code requirements. I don't have ASCE 7-95 with me here, but will try to locate it tonight.
Vincentpa: I agree IBC and ASCE has really made things difficult by not cooperating with each other to provide a single standard. I also agree that 2006 got better, and my understanding is that the trend of repeating info from the ASCE standard is being phased out future editions of the IBC.
I find the difference in wording between IBC and ASCE about stress increase interesting: IBC limits it specifically to wood design (1605.3.1.1), while ASCE is quite vague about it, leaving it "to be justified" (2.4.1). ASCE 7 also does not present the option for the "alternative basic load combinations"
There has been some suggestion that the building code is not a law (re: the 1st response to the OP), but "just a guide". A totally disagree with this. The use of the International Building Code was adopted as a law, at least in PA, by the Uniform Construction Code Statute and its amended acts. I will leave it to the legal minds as to the difference between the code being a law, and the requirement that specific codes be used is the law. But either way, it appears to me that not following the code is inconsistent with the state law. I would imagine other states or municipilaties have adopted the use of the code in some similar legal manner.
I also agree that, as engineers, we have to use our judgment. But it is also our responsibility to conform to the applicable building code(s). I cite the NSPE Code of Ethics for Engineers: Article II, paragraph 1b: "Engineers shall approve only those engineering documents that are in conformity with applicable standards." ASCE 7 is an applicable standard per IBC. I realize this is not "a law", but I believe it is worth considering as responsible professional.
Finally, the IBC actually does have a commentary that can be purchased separately. I quote:
"Previous editions of the model codes specified that the overturning moment and sliding due to wind load could not exceed two-thirds of the dead load stabilizing moment; however it was not typically applied to all elements in the building. In the code this limitation on dead load is accomplished through the load combinations. The applicable combination is 0.6D+W+H. This load combination limits the dead load resisting wind loads to 60 percent but it apples to all elements." (Re: 2006 IBC Code and Commentary, Volume II, page 16-18) Based on the commentary, I can't see how one could argue that the intent to use it for the design of cladding was "forgotten".
I realize many different municipalities have adopted different codes, and my reflections are based on the 2006 IBC and ASCE 7-05, which are the current codes in PA. I guess the point I have been trying to make here is that yes, we have to use our technical knowledge and judgment in our designs, but we also need to comply with the building code. Period. Without a doubt, the way the codes are written it is often difficult to interpret them. But I see no ambiguity in the load combinations required by IBC, no matter how much one disagrees with it. I will step off my soap box for one final time.
JKW