Process Chill Water Loop for Multiple Machines with varying requirement. 1
Kakit
I have a process chill water loop that has been serving 1 machine very well. We recently added a 2nd machine to the loop but having issue with getting flow through it without throttle return side of the header.
Header is 2" pipe
Machine 1, 2" pipe, 150GPM
Machine 2, 1" pipe, 50GPM
Pump runs at constant speed, no VFD
Take a look at the diagram, in order to get flow through 2nd machine, I have to throttle the "Return line shut-off valve" and "Machine 1 Return Line Shut-off valve".
We will be adding a 3rd machine soon and like have better understanding of how to setup chill water loop for multiple machines with varying requirements. I think the 2nd machine doesn't have enough pressure to overcome the header pressure, hence having to throttle the return header valve. What is the best option to resolve this without manually adjusting return header. Will adding a booster pump at machine 2 work?
Although I think a booster pump could be made to work, if your existing pump(s) have the head capacity for the added machines, then you could just add a balancing valve to the return side of both machine 1 and machine 2 upstream of the "Return Line Shut-off Valve" . The balancing valves can be manual or automatic, and they simply add a pressure drop to the loop to help get the flow you want through each loop - like what you're doing now with the hand valves. If you plan to keep adding machines, then automatic balancing valves may be best.
What about the pump performance - does it match the duty case Q- h requirement ?
Ask a process engineer to sort this out for you.
a) The "return line shutoff valve" can be replaced with a constant dP control loop, which should then act as a pump min flow control mechanism and provide a constant dp between supply and return headers, but I suspect this control valve should be relocated to be downstream of the filter.
b) What parameter controls what the required flow to each machine should be - is it the temp of some fluid within the machine ? If so, add a temp control loop to each machine to admit only the required flow and no more- this TCV can be either on the supply or the return line from each machine.
The flow velocity in 2 in header with a total 200 gpm flow is around 6 m/s, which is high. There will be a significant pressure drop in the header itself.
So, a thorough review of pipe sizes along with the pump head-capacity curve is required.
nice bow ties on your drawing, kidding!
You need to perform a full hydraulic study, 2 inches pipe for header is too small.
Pressure on the return line should me manage (PCV) to ensure all users get sufficient enough water.
My 2 cents
Pierre
If you dont want manually adjustment of return valves, you may consider to install FCV for each unit.
The velocity of flow for 200 GPM is around 6.4 m/sec. You need to conduct a hydraulic study to see if a booster is necessary . Without knowing the pump head-capacity curve and piping losses nothing can be suggested.
When you increase the size of your supply and return lines (to minimize pressure drop in them) your chiller may become the choke point.
How much cooling do you need?
How much flow do you need to do that?
Can you get buy without having all of you flow return through the chiller?
We did something like this with temperature sensing self-acting valves at the outlet of each machine.
There was also a bypass line on each one to assure a minimum flow.
I am not an expert on hydronic systems but it looks like you have it piped up wrong. You cannot take off of a single supply/return line and dump back into it unless you have individual pump units at each machine take off to force the flow through each machine. Without a pump at each machine take-off, you need a separate supply and return header.
With only one machine it was ok because it naturally formed a separate supply and return header. When you added the 2nd machine by extending the header, now the 2nd machine takes off and dumps into the same place basically as there is very little pressure drop from the point of take off to the point of return. The pressure drop in the header equals the pressure drop available for flow in the branch piping to the machine 2. That is why you had to induce a pressure drop with the valve between the point of take off and point of return to force the flow through machine 2. But when you did this you had too much pressure drop for machine 1 so it starved the flow to machine 2 unless you also throttled the valve to it.
You need to just disconnect the supply and return headers so that all supply flow goes through all machines and exits all machines into a separate return header. Or install secondary pumps at each machine.
See attached.
Agree with pierreick, a full hydraulic study by an experienced Engineer is called for.
When the 3rd machine is designed for, take a look at making the supply and return lines into loops. With bidirectional flow the existing header size might work.
Also agree, 2” header in one directional flow seems too small.
TCV’s on the return side of machines would improve the operation!
your system as others have noted is just too small to be extended. increasing flow has a squared association with pressure drop.
There are many details missing from your sketch including pump curves or duty points, lengths of the respective sections and elevation and also what the pressure drop is across the machine and where the third unit would be attached.
What worked for one unit clearly isn't going to work for two without changes.
also flow rates need to be considered at min flows or chiller flows, i.e. do you want to run with just machine 2 and machine 1 off? Then check minimum chiller flow.
Use of flow control valves or PICVs as the HVAC guys call them for some reason.
you prob need a 3" or maybe even a 4" header and return, fit each machine with PICVs and then control the opening of the end by pass to be a minimum DP. I.e as the pressure rises, open up flow to maintain a minimum flow then when if falls ad more chilled water is taken closes in to avoid wasting cold water
Or you can go for a primary / secondary system. Many ways to skin this cat.
