Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Recent content by Rocketir

  1. Rocketir

    3 phase faults

    You can think of three phase faults as an extreme case of high loading. Most of the time you don't have a perfectly balanced system and there will be neutral current. So if you have it during normal conditions why not during faults. The only difference is the impedances.
  2. Rocketir

    120/240 Y transformers.

    Thank you for the sanity check. ps. enjoyed the NeqSeq paper.
  3. Rocketir

    120/240 Y transformers.

    I had a customer request a 3phase 4 wire 120v l-n, 240v l-l wye connected voltage transformer. 120 l-n on each phase and 240 l-l across each phase. I had never heard of this? Does any utility use these? We currently have the 120/208 with three 120 l-n's and the 208 l-l. We also have the...
  4. Rocketir

    Use of Reclosers for Capacitor Bank Switching

    I have seen them used on a rural circuit with a small (600 kVAR) bank. We used a Nova recloser and operated on voltage. This was due to a large quarry type of customer causing large voltage flucuations on the primary. We would close instananeously during voltage dips.
  5. Rocketir

    Peak Demand Calculation

    Ask to talk with the Engineer at the utility, Not the customer rep. The Engineer will know the right answer for your application.
  6. Rocketir

    Sensitive earthfault settings

    Reminds me of a discussion we have had previously. http://www.eng-tips.com/viewthread.cfm?qid=80163 HTH
  7. Rocketir

    CAD designer with wrist & forearm pain seeking new career

    I am another one that votes for switching hands. I did it when a while ago because my primary hand was causing me pain. I didn't like that so I quit doing what was causing me pain. Switching to the left side also had the added benefit of being able to type with the right at the same time, as...
  8. Rocketir

    load loggers

    I have talked with these guys. http://www.natiscomm.com/ They have made us some load loggers for the underground. They are very flexible with their product, just tell them what you want. We were able to get a encrypted wireless datalogger. We have used the sensorlinks for the overhead and they...
  9. Rocketir

    Distribution Transformer Test

    Quench the arc to minimize the voltage dip. Try to test using the S&C Fault tamer fuse. http://www.sandc.com/products/faulttamer/default.asp Jes
  10. Rocketir

    Sensitive Earth Fault relay operation for faulted o/h lines

    <<Delay the SEF tripping so more faults will be cleared by the fuses. Unless it lands on somebody, downed conductor is not a safety hazard untill someone approaches it.>> I disagree. A conductor laying on the ground can cause fires. And if this results in a large forest fire it can result in a...
  11. Rocketir

    Sensitive Earth Fault relay operation for faulted o/h lines

    1. Settings adopted for such relays. Where we have used them we set them to 10% of the Grd trip setting. 2. Whether they face similar SEF relays operation caused by reasons other than fallen line conductors. If yes, what procedure do they follow to restore the supply? Do they patrol the whole...
  12. Rocketir

    Bury 15kV cables under Lake

    I assume the lake is too big to go around?
  13. Rocketir

    How do you calculate power usage? (Utility costs)

    KISS I total agree with peterb. It sounds the most logical.
  14. Rocketir

    OHL trip under foggy conditions

    I'm sorry I can't comment on the arching horns. But I would persue the relay reports to see if you are getting a fault in the same area each time. This would pinpoint a problem area rather than just suspect the whole line. After reading your problem, it brought to mind a problem I had with...
  15. Rocketir

    Fuse cutouts / expulsion drop-out fuses

    50-60% unknown cause is awful high. We occasionally have a weak link that just falls open or one that clears and doesn't fall down, but that is not the norm. We use a lot of fuses on our overhead tap lines and transformers. After a fuse operates we generally find a cause by patrolling the...

Part and Inventory Search